Enabling Ethernet Connectivity on Octoclock and Octoclock-G
- 1 Application Note Number
- 2 Revision History
- 3 Overview
- 4 Verify Current Octoclock Configuration
- 5 ATMEL-ICE Configuration
- 6 Thread Priority Scheduling
- 7 Adjust Network Buffers
- 8 Adjust Ethernet MTU
- 9 Increasing Ring Buffers
- 10 DPDK
- 11 Disable Hyper-threading
- 12 Disable KPTI Protections for Spectre/Meltdown
AN-800
Date | Author | Details |
2020-01-13 | Sam Reiter | Initial creation |
This application note covers, in detail, the steps required to program an Octoclock or Octoclock-G to allow Ethernet connectivity and communication with UHD. This guide serves as a supplement to the UHD Manual's coverage of the topic. In this guide, we will use Ubuntu 19.10 to program an Octoclock using an ATMEL-ICE programmer.
To get started, we want to make sure that this guide is appropriate for your device(s). Currently shipping Octoclocks will come with the following firmware pre-loaded. You can test which unit you have with a simple ping test:
- Connect the 6V DC power supply to the Octoclock
- Connect your Octoclock's RJ-45 port to a host PC via an Ethernet cable
- Configure your host's Ethernet port to a static connection with the IPV4 address:
192.168.10.1
- Configure your host's Ethernet port with a subnet mast of:
255.255.255.0
- Turn your host's Ethernet port off and back on for changes to take effect
- In a terminal, issue the command:
ping 192.168.10.3
A successful ping between devices means that your device is already configured with updated firmware and this guide is *not* necessary. At this time, this guide has not been tested for recovering bricked devices.
BREAK
Ensure your CPU governor is set to performance
. This can be done with the Linux utility cpufrequtils
Install cpufrequtils
with the command below:
sudo apt install cpufrequtils
You can then set the CPU governor to performance
per core by issuing the command:
sudo cpufreq-set -c $core_number -g performance
To set the CPU governor to performance
for all cores:
for ((i=0;i<$(nproc);i++)); do sudo cpufreq-set -c $i -r -g performance; done
You can then verify that the CPU governor has been set by running the command:
cpufreq-info
UHD Warning: Unable to set the thread priority. Performance may be negatively affected. Please see the general application notes in the manual for instructions. EnvironmentError: OSError: error in pthread_setschedparam
To address this issue, non-privileged (non-root) users need to be given special permission to change the scheduling priority. This can be enabled by creating a group usrp
, adding your user to it, and then appending the line @usrp - rtprio 99
to the file /etc/security/limits.conf
sudo groupadd usrp sudo usermod -aG usrp $USER
Then add the line below to end of the file /etc/security/limits.conf
@usrp - rtprio 99
You must log out and log back into the account for the settings to take effect. In most Linux distributions, a list of groups and group members can be found in the /etc/group
file.
This applies to Ethernet connected USRPs (N2xx, N3xx, X3xx, E320).
N2xx
sudo sysctl -w net.core.rmem_max=625000000 sudo sysctl -w net.core.wmem_max=625000000
X3xx/N3xx/E320
sudo sysctl -w net.core.wmem_max=576000 sudo sysctl -w net.core.rmem_max=33554432
Adjust Ethernet MTU
For 1 Gigabit connections, the MTU should be set to 1500
For 10 Gigabit connections, the MTU should be set to 8000
It is important to set the value and not leave it is automatic
This applies to Ethernet connected USRPs using a 10 Gb interface (X3xx, N3xx, E320).
Increasing the Ring Buffers on the NIC may help prevent flow control errors at higher rates.
DPDK
DPDK is supported on N3xx, X3xx and E320 USRPs. DPDK replaces the traditional Linux networking stack with a low overhead user-land based driver. Additional details of using DPDK can be found in the UHD Manual located at the following link: https://files.ettus.com/manual/page_dpdk.html
In some applications which require the highest possible CPU performance per core, disabling hyper-threading can provide roughly a 10% increase in core performance, at the cost of having less core threads. Hyper-threading can be disabled within the BIOs and varies by manufacturer.
In some cases, disabling the KPTI protections for the Linux Kernel can increase performance by 10-15%. It is important to note the ramification making this modification can have. This modification is only recommended for systems that absolutely require the best performance and are not connected to the internet.
- https://en.wikipedia.org/wiki/Meltdown_(security_vulnerability)
- https://en.wikipedia.org/wiki/Spectre_(security_vulnerability)
Disabling KPTI protections can be done by adding the lines below to your /etc/default/grub
file at GRUB_CMDLINE_LINUX_DEFAULT=""
pti=off spectre_v2=off l1tf=off nospec_store_bypass_disable no_stf_barrier
After modifying the grub
file, run the following command to update your configuration and reboot:
sudo update-grub